Hey yall I sure need some help please. I changed out a 6 spot to a 8 spot for my wifes grooming building.I went with a Eaton cause it was on sale. I didnt take a pic before I removed the wires at the bottom coming in to feed the panel from the main pole.I also put a additional ground bar but not sure it needed it. I am not a electrician but I do my best to make it all happen. When I removed the white and ground wire they were together in one spot on the bar and I put them back on the new one the same way. I just want to ask if it looks ok the way I got it.I know we should had got a electrician but I do have one coming when we put he new main pole in.I hope it was ok to put this in here beings its a home electrical issueThe panel I removed was a older square D. Anyway I sure appreciate yalls patience and time with me.

Note- I just seen the industrial forum,maybe a admin can move it for me--I apologize for the mess up.
 
Last edited:
The bare grounds are supposed to go to the ground buss with the green screws.
 
It also looks like the two breakers on the bottom right are 30 amp with 12 wire connected to them.
 
Not going to work the way it is wired, left side of box is dead. Grounds should be on the greens, whites on the neutral, Missing a black hot on the input, if this is a sub panel it needs ground rods and the ground wires isolated.
30 amp breakers with 12 ga. No No.

As chuckinnj nj would say time to call a pro
 
Oh shoot then the 12 size wire is to small and thats maybe why the other 30 amp breaker would get warm at times.
On second look, your actual main feed is wrong. Should be 2 hots, a neutral and a ground conductor.
Should I need to get a 4 wire set up and pull a new one by a chance from the main pole?
 
Not going to work the way it is wired, left side of box is dead. Grounds should be on the greens, whites on the neutral, Missing a black hot on the input, if this is a sub panel it needs ground rods and the ground wires isolated.
30 amp breakers with 12 ga. No No.

As chuckinnj nj would say time to call a pro
Yeah I sure may have to do that indeed my friend.
 
I don't know if that thing is fed 120V or 240V. Is the feed coming into the box a neutral or one leg of the 240 aka "hot?"

No idea if the capacity is anywhere near right for wire sizes, feed, etc.

What little I know about subs is they would normally be (if a 240 box) be fed with 4 conductors, AKA a green ground connecting to the box and the green ground bus, a white neutral going to an isolated/ insulated neutral buss, and two hots for the two 240 legs, AKA 120V to ground each.

Unlike a main, you can NOT connect the neutral and ground busses both to the box, or in some older boxes use one buss for both.
 
I see now what yall are saying about the sub panel white and ground wire needs to be separate in the Neutral Bar and the Ground bar.
 
Is that a sub panel? Show a pic of the panel that is feeding this.
Yes sir using it for the sub panel---I will find a pic of the other one on the main. Its like 30 years old and the post is splitting bad and carpenter bees has destroyed the inside of the 6x6. Thats why I had to start setting up a new post. I didnt do the work on it(Main).
 
Here is the main-please excuse the wire that is not connected cause we had to change it out to the pump house
 
The black and white wire going to the 60 amp breaker on the right hand side is going to the sub panel I am working with now
 
The bare grounds are supposed to go to the ground buss with the green screws.
Can you please look at the pic of the sub panel and I did have to buy a ground bar and it had a screw and small piece and I put it on the neutral bar. I think now this is wrong and should I even need to use it? I guess the white neutral goes to the Neutral Bar that is factory installed and the Ground goes to the green ground that I installed. Should I need to add the ground screw and the small piece that came with it?I think they were calling it a bonding tab.Oh shoot the ground that I got coming in with the feed,Does it actually go to the ground bar I added?
 
If I look at this correctly. Technically with a sub panel you should run a 4 wire 2 power black 1 white neutral and bare ground or green wire then you have to get a neutral bar that is insulated from the box remove the stripe that tie the neutral to the ground bars so that the neutral is separate from ground .
It's confusing but neutral and ground are the same .you are running 3 wires and made the white wire power along with the black wire you can get away with it just run the bare ground wire to the ground bar and put all your white neatrals on the ground bar it will work
 
OK so now that you have shown your main box, you do have a functioning sub panel. It is not to code but would be correct for 20? years ago. To make it correct you need to change out the feed wire to a 4 wire conductor, black red white green, add ground rods and split the neutrals and grounds.
Wrap a piece of black tape onto the white wire to show it is a hot conductor.
 